DC and AC circuitbreaker>>>?

MAGICPIE3FOCUSPOWER said:
Hi All! 8)

I am a little bit confused while looking for some circuit breaker.
What is/are the difference(s) between AC and DC circuitbreaker?

Thanks for help!


AC is alternating current and every time it cross the 0 volt when changing polarity this blow the arc that the Dc current like to produce. Normally the design of a DC fuse and breaker are different and more complicated. if you use a 32V max fuse ( found on the 12V car) to cut 100V dc there is a risk of when the fuse blow, the arc that is created continue to live for few second and it make everything to melt around due to the intense heat.. this can cause a fire. this is not a problem with AC because the voltage change and cross zero witch blow the arc 120 times per second.

Dc fuse and breaker have longer gap between the contact and this reduce the arc problem.

you can get some decent quality circuit breaker here for DC up to 150V

some popular are the Airpax of 80V.. but there is also some 150vdc one.

Some have screw and some have already the bullet connector!! :D

MidNite Solar DC Circuit Breaker MNEPV
http://www.cafr.ebay.ca/itm/8A-10A-...-Breaker-disjoncte-Solar-Charge-/271147082582

Airpax:
http://www.ebay.com/itm/Airpax-LELK1-1REC4R-32969-80-V-DC-BREAKER-80A-/111394715244

Doc
 
Doctorbass said:
MAGICPIE3FOCUSPOWER said:
Hi All! 8)

I am a little bit confused while looking for some circuit breaker.
What is/are the difference(s) between AC and DC circuitbreaker?

Thanks for help!


AC is alternating current and every time it cross the 0 volt when changing polarity this blow the arc that the Dc current like to produce. Normally the design of a DC fuse and breaker are different and more complicated. if you use a 32V max fuse ( found on the 12V car) to cut 100V dc there is a risk of when the fuse blow, the arc that is created continue to live for few second and it make everything to melt around due to the intense heat.. this can cause a fire. this is not a problem with AC because the voltage change and cross zero witch blow the arc 120 times per second.

Dc fuse and breaker have longer gap between the contact and this reduce the arc problem.

you can get some decent quality circuit breaker here for DC up to 150V

some popular are the Airpax of 80V.. but there is also some 150vdc one.

Some have screw and some have already the bullet connector!! :D

MidNite Solar DC Circuit Breaker MNEPV
http://www.cafr.ebay.ca/itm/8A-10A-...-Breaker-disjoncte-Solar-Charge-/271147082582

Airpax:
http://www.ebay.com/itm/Airpax-LELK1-1REC4R-32969-80-V-DC-BREAKER-80A-/111394715244

Doc


hey doc do you know if you can parallel those DC breakers to handle higher amps? ie 2x the 60A breakers for 120A?
 
While there is a range of performance for each fuse and circuit breaker design, they are similar and rarely would one need to use both.

Paralleling generally works but the current might not split perfectly equally so the full rating could end up being a bit less than 2x.

Look at the data sheets, a breaker will carry larger currents for a while, depending on temperature. You may not need two in parallel.

Watch the polarity on DC breakers, it needs to be right for the ARC to extinguish quickly.
 
I paralleled a lot of fuse and it work just perfect. they blow when they have to and they hold when they have too. As for circuit breaker I never paralleled any but this is my actual plan for my Max-E.

The actual max battery current is 130A and I should rarely sustain that level for more than 10 sec ( ex: for acceleration)

I have bought one 100A ( trip at 125A after 52 sec) and two other that I might parallel if the 100A trip or trip too often.

The two other are one 50A and one 60A ( aprox 110A parallel) and about 150A trip after 52 sec.

I wiil test.

Before for a 12kW ebike I was using 3 parallel 40A fuse (the 12V car fuse) and they did their job as they should And I think that the fact that there is many in parallel is a way to blow the arc progressively because I never had arc problem at 24s lipo and even 30s lipo for these 12V fuses.

Doc
 
MAGICPIE3FOCUSPOWER said:
Thanks!

Do you have to use a precharge resistor when using DC circuitbreaker?
Or it is just overkill?

Yes Precharge must be installed. Breaker or fuse don't replace precharge.

Doc
 
striker54 said:
Doctorbass said:
MAGICPIE3FOCUSPOWER said:
Thanks!

Do you have to use a precharge resistor when using DC circuitbreaker?
Or it is just overkill?

Yes Precharge must be installed. Breaker or fuse don't replace precharge.

Doc

Actually, adaptto guys say that a precharge is not needed if we use a breaker.

Well it depend on what we are talking about... the first time you connect the battery to the controller YOU MUST have a precherge, temporary or permanent. Then the adaptto controller is always connected to the battery and alwys seeing full battery voltage, but it's because it have a sleep mode wich is great! but not all controller does
 
MAGICPIE3FOCUSPOWER said:
Thank you very much!!! 8)

I see you are using 330 ohm precharge resistor is 150 ohm also suitable?
Due I have some 150 ohm 10W laying around :mrgreen:

100ohm would be fine for most setups... and 3w is generally enough too. pretty sure that's whats on my current build
 
Doctorbass said:
striker54 said:
Actually, adaptto guys say that a precharge is not needed if we use a breaker.

Well it depend on what we are talking about... the first time you connect the battery to the controller YOU MUST have a precherge, temporary or permanent. Then the adaptto controller is always connected to the battery and alwys seeing full battery voltage, but it's because it have a sleep mode wich is great! but not all controller does

shouldn't an AC braker be able to precharge (a bit)?
I think of if many electrical gadgets are connected to sockets in the house and the braker will be closed. I believe there would be a BIG spark if it wouldn't do some kind of precharge..
 
Maybe this help?

1277710967638_hz-myalibaba-web6_7593.JPG
 
Some AC circuit breakers also do DC too, you just need to check the spec.
 